On Wed, Nov 4, 2009 at 6:38 PM, <nevin@enginehosting.com> wrote:
> The 2002 press release is talking about the Fremont 1 facility not the
> newer Fremont 2 facility. Fremont 1 has a fixed power availability to each
> cabinet of just a single 15A circuit. You can not modify or change that,
> and if you need more power your option is to add another cabinet. You are
> not allowed to route power cords between cabinets so you are forever running
> a single circuit and 80% of your 15A circuit max. The data center was built
> in a different time.
>
A different time, but obviously not that much different...
Fremont 2 is still limited to either a single 15A or a single 20A circuit
per rack.
They are rebuilding one of the Fremont 2 wings and turning it into a single
area rather than the existing suites, so it'll be interesting to see if
things are done differently there.